ADC read problem

Post by GTF »

Hello All,

I am working with an 18F14K50. A portion of my program is intended to detect the minimum 10 bit PWM duty cycle required to initiate a position change. I am first reading the pot with the PWM disabled, then continuously re-reading as the PWM is gradually increased. What I have noticed is that if my target is less than .03 to .04V greater than the initial reading, the loop ends on the first pass. There is actually a fair bit of movement required in order to see this much change in the pot output. i.e. the first loop read is already greater than the initial read by at least .02V A meter connected to the circuit does not show any change. I see the same behaviour if I read the ADC as int.

I have attached a short example of what I am doing in this section of the program. Any help is appreciated.
Attachments
ADC_test.fcf
(12 KiB) Downloaded 281 times

User avatar
Enamul
Posts: 1772
Joined: Mon Mar 05, 2012 11:34 pm
Location: Nottingham, UK
Has thanked: 271 times
Been thanked: 814 times
Contact:

Re: ADC read problem

Post by Enamul »

What I have noticed is that if my target is less than .03 to .04V greater than the initial reading, the loop ends on the first pass.
0.02 v is your condition mentioned in the program 0.03 is greater than 0.02 so program should pass the loop..I might be completely don't understand what you are trying to say..
There is actually a fair bit of movement required in order to see this much change in the pot output.
this small amount of change is not easy to see.
the first loop read is already greater than the initial read by at least .02V A meter connected to the circuit does not show any change.
where is the meter connected and what change you are expecting and what you can't see..
If you use trimmer resistor to tune ADC voltage, you should be able to see initial value and initial + 0.02 V in LCD (if you have any)..so that you can certainly say program works fine or not..
Attachments
ADC_test.fcf
With LCD
(17.5 KiB) Downloaded 281 times
Enamul
University of Nottingham
enamul4mm@gmail.com

GTF
Posts: 170
Joined: Sat Dec 10, 2011 7:21 pm
Location: Canada
Has thanked: 20 times
Been thanked: 52 times
Contact:

Re: ADC read problem

Post by GTF »

Hello Enamul,

Sorry if my post was confusing. The .02V is just an example of a value that will not work because of this problem. I actually would like to use a value of only .005V or so, but am forced to use a value greater than .03V, which is at least 1 degree of rotation of the mechanism and is clearly visible. Otherwise the loop ends on the first pass, as if the ADC input is already greater than the initial read plus .02V. I am placing the test meter at the input pin of the 18F14K50.

User avatar
Enamul
Posts: 1772
Joined: Mon Mar 05, 2012 11:34 pm
Location: Nottingham, UK
Has thanked: 271 times
Been thanked: 814 times
Contact:

Re: ADC read problem

Post by Enamul »

Hi,
What is the maximum voltage you might need to measure? As for higher resolution like something you are looking for, I think you need to reduce Vref which will provide higher resolution..
For example, Vref=5V reading as INT, resolution is 5V/1023 = 0.00488V but same could be 1.25V/1023 = 0.00122V
Enamul
University of Nottingham
enamul4mm@gmail.com

GTF
Posts: 170
Joined: Sat Dec 10, 2011 7:21 pm
Location: Canada
Has thanked: 20 times
Been thanked: 52 times
Contact:

Re: ADC read problem

Post by GTF »

The max value is approximately 4.5V. My current Vref/VDD is 4.75V

I have also done the same thing in the reverse direction. In that case the target to end the loop is a value slightly below the initial read, and there seems to be a similar offset occurring. In both cases the first loop read is always some fixed amount greater than the initial read. edit: it is never lower than the initial read
Last edited by GTF on Wed Sep 12, 2012 7:13 pm, edited 1 time in total.

User avatar
Enamul
Posts: 1772
Joined: Mon Mar 05, 2012 11:34 pm
Location: Nottingham, UK
Has thanked: 271 times
Been thanked: 814 times
Contact:

Re: ADC read problem

Post by Enamul »

OK..I will try to sort that using INT read..I guess I can sort that. I will let you know..
Enamul
University of Nottingham
enamul4mm@gmail.com

GTF
Posts: 170
Joined: Sat Dec 10, 2011 7:21 pm
Location: Canada
Has thanked: 20 times
Been thanked: 52 times
Contact:

Re: ADC read problem

Post by GTF »

Here is a new example and video demonstration. This one runs in both directions ( 2 loops). I corrected errors in the earlier example where I did not select "10 bit" duty cycle. My actual project code does not have that error.

This time I added 1 sec of PWM activation at a DC of 600, followed by a 5 second recovery period, prior to each initial read. This was to check if the pot always returns to the same start point. You will see the first one as a fluctuation in the meter reading as soon as the reset switch is pressed. The green LED is flashing while the first loop is running. Then there is another 1 sec of 600 DC and 5 sec recovery during which the red LED is on solid. Then a new initial read is done. Next the red LED should be flashing while the second loop runs. This does not happen. At the end of the program both LEDs are on solid.

You can see that the first loop does not end until the ADC read is almost double the desired .005V above the initial value. Because the second loop does not run at all, it appears that the ADC read on the first pass is interpreted as already more than .005V below the initial reading...... Although on the meter there has been no change.

video: http://dl.dropbox.com/u/65295456/ADC%20Test.wmv ....allow a minute for the file to load

In this example the second loop will run briefly if I increase delta to .03V rather than .005V. The first loop in this example actually runs with a delta of .005V, but that does not work in my project code.

Thanks

Grant
Attachments
ADC_test2.fcf
(17 KiB) Downloaded 290 times

GTF
Posts: 170
Joined: Sat Dec 10, 2011 7:21 pm
Location: Canada
Has thanked: 20 times
Been thanked: 52 times
Contact:

Re: ADC read problem

Post by GTF »

Here is what the 18F14K50 is reporting via USB to serial vs what my meter reads. The int reads of 755, 757, 759, 755 correspond to meter values of 3.490, 3.496, 3.492, 3.490V. The second int neutral read is always greater than the preceding int read even though it is less(and should be) on the meter.
Attachments
ADCAccuracy.jpg
ADCAccuracy.jpg (22.69 KiB) Viewed 8268 times

User avatar
Enamul
Posts: 1772
Joined: Mon Mar 05, 2012 11:34 pm
Location: Nottingham, UK
Has thanked: 271 times
Been thanked: 814 times
Contact:

Re: ADC read problem

Post by Enamul »

I see.. :!:
I will check in hardware to replicate the situation
Enamul
University of Nottingham
enamul4mm@gmail.com

GTF
Posts: 170
Joined: Sat Dec 10, 2011 7:21 pm
Location: Canada
Has thanked: 20 times
Been thanked: 52 times
Contact:

Re: ADC read problem

Post by GTF »

Here is the problem. The calibrated minimum Duty Cycle for 1 direction ends up too low (and possibly too high the other direction).
Image
I have attached the Flowcode I used for this experiment.

Edit: added some comments to the flowchart
Attachments
Min_Duty_Cycle_Cal.fcf
(27.39 KiB) Downloaded 284 times

GTF
Posts: 170
Joined: Sat Dec 10, 2011 7:21 pm
Location: Canada
Has thanked: 20 times
Been thanked: 52 times
Contact:

Re: ADC read problem

Post by GTF »

More odd behaviour......
If I disable the second read of the neutral position it is the first minimum duty cycle determination that does not work correctly. Although the targeted position change is reported, there was no change in voltage on the meter, no movement and no PWM applied.

In this case the disabled section of the flowchart does not occur until after the section that does not function correctly!

Image

Image

zadah
Posts: 31
Joined: Wed May 02, 2012 5:49 pm
Has thanked: 3 times
Been thanked: 7 times
Contact:

Re: ADC read problem

Post by zadah »

Have you tried filtering capacitor on input pin of the PIC?

How about different potentiometer with lower resistance?

GTF
Posts: 170
Joined: Sat Dec 10, 2011 7:21 pm
Location: Canada
Has thanked: 20 times
Been thanked: 52 times
Contact:

Re: ADC read problem

Post by GTF »

zadah wrote:Have you tried filtering capacitor on input pin of the PIC?

How about different potentiometer with lower resistance?

There is a 470nf cap and a 100k pulldown on the circuit. The pot is already proven with other controllers/firmware.

I have also tried multiple samples/averaging with the same results. My impression is that the values being used in the calculations can be off by multiple times the theoretical ADC resolution. So for example, the current position can be determined to be on the opposite side of the stored neutral position than it actually is, requiring the use of a wider than acceptable deadzone.

The stored values appear to be consistent when read back multiple times, so perhaps the problem is inconsistency in the ADC conversion.

GTF
Posts: 170
Joined: Sat Dec 10, 2011 7:21 pm
Location: Canada
Has thanked: 20 times
Been thanked: 52 times
Contact:

Re: ADC read problem

Post by GTF »

Although further testing is required to confirm desired operation, it seems my CPU clock speed was low.